Just curious if it could be wired to a 3P 415v input PDU like this:Because that's a European unit L1 to Neutral is 230v.
And 3 units combined for 3-phase will be 400v/230v.
Line to Line is 400v
Line to neutral is 230v.
You can't use this 3-phase configuration for North American 240v equipment.
I'm off grid in the USAWHERE are you located Marty?
YesJust curious if it could be wired to a 3P 415v input PDU like this:
Thanks for the quick reply.Yes
But, that still doesn't solve the problem of trying to power North American 240v loads.
I don't know anything about crypto mining equipment.Thanks for the quick reply.
The PDU input is 415v, output is 230v, and it has C19 and C13 plug receptacles. My equipment requires two C13 inputs at a voltage between 200-240v. So wouldn't this PDU simplify what I am trying to sort out, or perhaps I misunderstand what you mean?
Here's the equipment:
They have their own power supplies: https://support.bitmain.com/hc/en-us/articles/900001205726-APW12-12V-15V-SpecificationI don't know anything about crypto mining equipment.
If they have isolated power supplies, they might work with European power.
With DC output, they are probably isolated.They have their own power supplies: https://support.bitmain.com/hc/en-us/articles/900001205726-APW12-12V-15V-Specification
Thanks for your input. To clarify, should I ask the manufacturer if the power supplies are isolated and compatible with European power standards?With DC output, they are probably isolated.
But that's just my guess. I didn't see anything that said definitely.
Yes, that's what I would do.Thanks for your input. To clarify, should I ask the manufacturer if the power supplies are isolated and compatible with European power standards?
Because somewhere in there is a joke about wearing a hard hat to an electron fight.Caution: Wrong input voltage may probably cause miner damaged
Thanks for the input. This may be the easier option but it would be semi-outdoors.How about this one instead, single 220-240v output and can be paralleled upto 6
Now we know you are powering computers, I would say the ground issue is not a big deal to you are you are not going to be touching them much, unlike say an air compressor or lathe.
11KW MAX (11KW 48V) – Maximum Solar Online
maximumsolar.online
After lots of researching I decided I was complicating things and decided to go with six of the LVX6048 WP PV Inverters capable of 120/240v.Keep us updated, should be interesting
This would be best. If you plan on pushing the system hard.I’m wondering if I should go with 1000A busbars to be safe?
One way to look at it:After lots of researching I decided I was complicating things and decided to go with six of the LVX6048 WP PV Inverters capable of 120/240v.
I discussed this with Signature Solar and they said I needed a 600A busbar, 30000/48v, but that doesn’t seem safe.
I’m going to have three 16s 48v 280Ah battery packs max 1C. My loads can hit a maximum of 33,000 watts.
Is my math correct that I should have a 800 amp busbar:
33000w/.91 (DC to AC) efficiency /48v = ~755 amps
LVX6048 WP PV Inverter Manual
The manual mentions that the Battery Max Discharge is 150A. 150A x six inverters = 900A. 900A x 48v = 43,200w.
I’m wondering if I should go with 1000A busbars to be safe?
Appreciate any help!
So it sounds like
So it sounds like 50hz is the