Update on my site...
About three weeks ago, we had a grid outage, and with a fully charged battery, the system instead of running off battery, went right to generator.
I opened a case with SolarEdge and contacted my installer. After a few days, SolarEdge responded and told me to have the installer come out, and in the interim, they were updating the firmware of inverter 4.19.36->4.20.32 (two revs newer). The release notes for 4.19.36 had indicated "seamless transition to backup", which is why we thought it would have worked previously, but it was not. I don't see anything in the 4.19.39 or 4.20.32 that mention anything about backup changes, but maybe it was a small change and not reported.
Today, the installer showed up and connected to the inverter. SetApp initiated another update, which updated the firmware to 4.20.36 (one rev newer). Again, I don't see anything in the release notes, about backup related changes. In any case, this is what we saw...
There is a pull switch on the BackUp Interface that disconnects from the grid. We had a mostly cloudy day, 42% charge on our 16 kWh battery, and the house load was close to 1kW.
Upon disconnect, there was about a 2-3 second delay and it switched to battery AND PV. As the cloud cover was fluctuating, it would switch from powering the house from PV to battery to both. Looked good, and the battery was actually slowly charging.
To simulate the battery hitting the low charge limit, the installer changed the configuration so that the limit was a few percent below current charge. We then flushed toilets (well for water), ran microwave oven, turned on table saw, drill press, grinder, and a few other tools to start drawing down the battery. PV was bouncing between 500W and 2.5kW, so we were trying to draw more.
Eventually, it hit the limit and switched over to generator (I can't recall how fast, but seemed quicker than from grid to PV/Battery). Again, seemed to work well. The only issue was that, looking at the monitoring app on my phone it only showed how much PV was producing and that it all was going to battery. There was no indication of the house consumption, like I'd see if on grid, PV, and/or battery.
We were not able to test the system, when running on generator, switching back to battery at some point, once the battery is charged back up. It was late in the afternoon, and with the mostly cloudy sky, it would be hours before PV could recharge the battery, if at all today.
Grid was then turned on. It takes like five minutes to switch back to grid. Installer said that it monitors/tests grid power and PV, before switching to grid + PV.
Before leaving the installer set the configuration to switch from battery to generator, when battery is at 10% (factory min is 6%).
I reported back to SolarEdge, as to what happened and mentioned these comments/questions:
- There is no reporting of consumption, when running on generator and that I expected that it would, since generator is tied into the BUI.
- The generator powered the house, but was not recharging the battery, which their documentation indicates that it is supposed to do that.
- I asked them what the charge level of battery would have to get to, in order to switch from generator, back to battery. It didn't seem to be programmable from SetApp, according to the installer.
So, 95% of what we expected to see was working. It was switching to battery on grid fail, and then to generator. The battery was getting recharged by PV. The big item is #2, whereas #3 is minor (assuming it switches back), and #1 is a nice thing to have, but not required.