Hi,
Had working for months
Solis 3.6kw inverter, 4.6 PV.
x2 Pylontech US5000
Alarm 186B2 "No battery" from inverter yesterday, 40% charge, CAN OK.
no charge lights on batteries, just flashing Run.
Turned everything off, left few minutes & back on & all was working.
Done the same just a few hours ago.
47% charge & CAN seems OK.
turned everything off/on again, still Alarm.
On battery, various SW button pressing, 5 seconds 15 seconds On/Off
no charge LED's, just flashing run again.
Disconnected 2nd battery & left just x1 US5000 attached.
Battery Off & ON & SW. now working on that one battery & have the 3 charge LED's.
2nd battery disconnected. On/Off SW etc. Just the run LED.
Could it be that they have got out of Sync & battery 2 is really flat by noon as reporting 47% charge & upsets inverter.
Will try just the other battery overnight when it's charged off grid but would be really good to get a handle on this.
Thanks I/A
Had working for months
Solis 3.6kw inverter, 4.6 PV.
x2 Pylontech US5000
Alarm 186B2 "No battery" from inverter yesterday, 40% charge, CAN OK.
no charge lights on batteries, just flashing Run.
Turned everything off, left few minutes & back on & all was working.
Done the same just a few hours ago.
47% charge & CAN seems OK.
turned everything off/on again, still Alarm.
On battery, various SW button pressing, 5 seconds 15 seconds On/Off
no charge LED's, just flashing run again.
Disconnected 2nd battery & left just x1 US5000 attached.
Battery Off & ON & SW. now working on that one battery & have the 3 charge LED's.
2nd battery disconnected. On/Off SW etc. Just the run LED.
Could it be that they have got out of Sync & battery 2 is really flat by noon as reporting 47% charge & upsets inverter.
Will try just the other battery overnight when it's charged off grid but would be really good to get a handle on this.
Thanks I/A