SMA Sunny Boy inverters SB7.7-1SP-US40 and SB6.0-1SP-US41 have a "Secure Power Supply" (SPS) component, which can be wired to a separate SPS outlet. It can provide up to 2kW of 120V AC power in SPS mode in case of a grid failure. In such a case, it must be manually activated via an SPS switch.
Both "Neutral" and "Hot" wires in SPS are separate from the main "Hot" and "Neutral" wires in grid-tied circuits.
Does anybody know if the SPS "Neutral" is bonded with the main "Neutral" inside the inverter? Is it safe to make such bonding outside of it?
The idea is to use a common house "Neutral" for both SPS and grid-tied lines and a relay as an "Automatic transfer switch." It should automatically transfer power for the most critical 120V circuit in the house to the SPS in case of a grid failure.
It should work this way:
Both "Neutral" and "Hot" wires in SPS are separate from the main "Hot" and "Neutral" wires in grid-tied circuits.
Does anybody know if the SPS "Neutral" is bonded with the main "Neutral" inside the inverter? Is it safe to make such bonding outside of it?
The idea is to use a common house "Neutral" for both SPS and grid-tied lines and a relay as an "Automatic transfer switch." It should automatically transfer power for the most critical 120V circuit in the house to the SPS in case of a grid failure.
It should work this way:
- If the grid is active, the solenoid in the relay is energized and holds "Normally closed" contacts in the "Open" status. Those contacts are connected to the inverter as an "SPS activation switch." Thus, when the "Grid is on," the SPS is NOT activated.
- If the grid fails, the relay is not energized, and those "Normally closed" contacts will close and activate an SPS.
- Another contact group in the relay will transfer the "Hot" wire in the critical house circuit (server, telework computer, network equipment, etc.) from the main house panel (with no power at this time) to the SPS output in the inverter.
- Computers and network equipment all have their own UPS blocks. So, short power hiccups of up to 5-10 minutes each are not critical as long as the SPS can provide power for them within that timeframe.