Dzl: thanks for the very reasoned response. Its interesting that the West Marine Table you reference pointedly states that its for 12 V systems only. That leads one to think that the same table for 24 V or 48 V systems would be considerably different. So again, voltage matters?
Yeah, I was confused/bothered by this as well. One possible implication is that voltage matters.
How often is 24V-48V DC used in a marine setup? IDK. They may say 12V because their source has not tested it in a 24V-48V system.
Just a SWAG on my part.
Pretty often if we are talking about 24v, I believe we can largely thank the marine industry for the abundance of components available at that voltage compared with 48v.
The actual ABYC source material that West Marine is basing their chart on has tables for 12 and 24 (not 48). I was planning to put together a post on it, but that might take me a while so for now I'll link to the PDF and point to the relevant page numbers (note this is the 2008 edition, 2018 edition may be different but it looked like it would cost me $195 to find out).
Ampacity table for DC and AC circuits (single wire/not bundled) - Pg 60 of PDF
3% Voltage drop tables for 12v and 24v - Pg 67 of PDF
Relevant explanation of wire sizing - Pg 28-30 of PDF
11.14.2.5 Conductors used for panelboard or switchboard main feeders shall have ampacities as determined in E-11.8.1.1. Conductors used for branch circuits or in electrical systems that do not use a panelboard or switchboard shall have their ampacities determined by their loads (See 2TABLE II).
11.14.2.6 Voltage Drop - Conductors used for panelboard or switchboard main feeders, bilge blowers, electronic equipment, navigation lights, and other circuits where voltage drop must be kept to a minimum, shall be sized for a voltage drop not to exceed three percent. Conductors used for lighting, other than navigation lights, and other circuits where voltage drop is not critical, shall be sized for a voltage drop not to exceed 10 percent.
11.14.2.7 Conductor Size - To determine conductor size and insulation temperature rating, use the ampacity as specified in E-11.14.2.5 in conjunction with TABLE VI. Then use TABLE IX or TABLE X to check the conductor size for compliance with the maximum allowable voltage drop specified in E-11.14.2.6. In the event of a conflict between the ampacity table and the voltage drop tables, the larger conductor size shall be used.
11.14.2.7.1 To use TABLE IX and TABLE X , measure the length of the conductor from the positive power source connection to the electrical device and back to the negative power source connection. Use the conductor length, the system voltage, and the ampacity as specified in E-11.14.2.5, in conjunction with the appropriate volt drop table, i.e., three percent or 10 percent – TABLE IX or TABLE X, to determine conductor size
NOTES:
1. The power source connection may be the battery, or a panelboard or switchboard, if used.
2. If the ampacity as specified in E- 11.14.2.5 exceeds the ampacities in TABLE IX and TABLE X, the conductor size necessary to keep voltage drop below the maximum permitted level may be calculated by means of the following formula:
CM = ( K x I x L ) / E
Where:
CM = Circular mil area of conductor.
K = 10.75 (constant representing the resistivity of copper)
I = Load current in amperes
L = Length of conductor from the positive power source connection to the electrical device and back to the negative power source connection, measured in feet.
E = Maximum allowable voltage drop at load in volts (e.g., for a three percent voltage drop at nominal 12V, E= 0.03 x 12 = 0.36; for a 10 percent voltage drop at nominal 12V, E = 1.2). 3.
UseTABLE XI or TABLE XIIto convert circular mils (cm) to conductor gauge. If the cm area falls between two gauge sizes, the larger conductor shall be used
11.14.3.1 Conductors shall have a minimum rating of 600 volts.
11.14.3.2 Flexible cords shall have a minimum rating of 300 volts.
11.14.3.3 The temperature rating of conductors and flexible cords shall be at least 140F (60C) dry. NOTE: Conductor rating temperatures refer to the insulation maximum operating temperature of the conductors.
11.14.3.4 All conductors and flexible cords shall meet the flame retardant and moisture resistant requirements of UL 83, Thermoplastic-Insulated Wires and Cables.
11.14.3.5 All conductors and flexible cords shall meet the requirements of the applicable standards of Underwriters Laboratories Inc.
11.14.3.6 Conductors and flexible cords shall be stranded copper according to TABLE XI.
NOTE: Some currently available wire types that meet all of the above requirements are listed in Table VIII.
11.14.3.7 Conductors and flexible cords shall be of size according to TABLE VI and TABLE XII.
14.3.7.1 Where single conductors or multi-conductor cables are bundled for a distance greater than 24 inches (610 mm), the allowable ampacity of each conductor shall be reduced as shown in TABLE VI and TABLE XII .
NOTE: When determining the allowable amperage of bundled conductors using TABLE VI and TABLE XIII, the AC grounding conductor and a neutral conductor that carries only the unbalanced current from other conductors are not considered to be current carrying conductors.
11.14.3.7.2 The AC grounding conductor shall be permitted to be one size smaller than the current carrying conductors on circuits rated greater than 30 amperes.