EastTexCowboy
Solar Wizard
I have a question on cabling past a Y connector. I'm installing a system with 16 445W panels, a MPP 6548 invertor, and at least 2 of the EG4 5kwh batteries. The panels will be in four arrays with four in each array in series. By my calculations that's about 200W and 11 amps per array before the Y and 200W and 22 amps after combining two arrays with the Y. I'm going to have to run about 135' on the longest run (maybe a little less but I'm allowing a little extra). I have a good location for a Y connector about 60' from the panels. If I install the Y and I'm running 10 awg pv cable from the panels to the Y, can I continue with 10 awg cable for the remainder of the distance? What I'm not sure about is how the Y connector impacts the cable length. If I were carrying 22 amps for the entire distance I would have to go with 8awg based on the online cable size calulators. Since I'm splitting it I'm not sure. Here's a rough sketch.
Any advice much appreciated! I'm going to have another post about the whole earth ground, equipment ground thing and my head is spinning from so many videos and opinions on correct grounding. But that's for another day.