LiPO4 cells have an internal resistance on the order of 500uOhm, so Ohm's law would predict a fault current on the order of 48/.5 kA or about 96kA. That is really large, so large in fact, that there isn't a lot of equipment out there with that high of a SCC rating. Another issue is that it is DC. AC over current protection devices rely on phase reverse to extinguish the arc when the device opens. DC has no such phase reversal, so reliance is placed on an inert material like sand to extinguish the arc. As a result, at high fault current levels, it is tricky to safely interrupt.
One thing working in your favor is the resistance associated with the series cell wiring, wiring to "the outside world", and connections. These resistances will tend to swamp the cell resistances, maybe by a factor of two, so your available fault current may only be 1/3 to 1/2 the 96kA figure.
Perhaps Eve offers some data on cell impedance or resistance to allow a better analysis.
I would proceed assuming an available fault current of 32 to 48kA and find an OCP device with that level of AIC.
Hope this helps!