For sure EG4 team will cover it, and I hope
@ckenny can be happy with the performance in the end.
I will share a comment from my colleague Andy in the tech-support team. he started to support Luxpower users in the EU and Africa in 2018.
as below:
Regarding the tech support question from Colin, I can offer him my experience.
If there was a problem with 18kW MPPT, then it should be common among all machines. This is not the case, so it means we have to find the solution in the client Installation.
9 x 460w string in series = 4140w/string, which is well within the MPPT range.
The fact that the power increases then suddenly drops, to me indicates that the current carrying capacity of the cable connections (between Mc4 connectors and the bootlace ends going into the terminal block) is compromised somewhere.
The client might check the following:
Are all the Mc4 connections good, especially the terminations he made? It's important to bare the cable ends properly and make sure the metal part is pushed all the way up into the plastic housing.
Also check that the pv cable ends going into the terminal block is good.
Voltage (potential difference) can be measured on one strand of copper, but current cannot.
In other words, a weak connection will show voltage but will not be able to carry full current.
Thanks.
@Markus_SignatureSolar