I have (2) EG4 48v 100ah batteries from SS. They are in parallel and charged to ~53vdc. I have a shutoff switch with a fuse going to a VFX3648 inverter. I'm using a Classic Lite 150 cc which is not in the circuit. I turn on the breakers for the batteries and everything looks fine, but when I close the switch to the inverter, the batteries going into a fault condition - the red light goes on. I tried running the battery monitoring software that came with the batteries, but it doesn't seem to be working. The only thing I know to do is hook up (4) 12v batteries in series to see if the inverter comes on. Which is what I did several years ago and it worked.
batt settings.jpgonoff switch.jpgbms1.JPGbms2.JPG
 
The bms has probably tripped on the in-rush current to fill the inverter's capicitors.
The battery has an built-in pre-charge circuit.
The doco should explain how to use it.
 
I think you need to turn the breakers on both batteries OFF, then turn your inverter control switch ON, then lastly turn your battery breakers ON. This will engage the pre-charge circuit in the battery to prevent the inverter inrush from tripping the BMS.
 
OK, I hadn't thought of doing that. That makes more sense. I'll try that right now and let you know how it goes.
 
I think you need to turn the breakers on both batteries OFF, then turn your inverter control switch ON, then lastly turn your battery breakers ON. This will engage the pre-charge circuit in the battery to prevent the inverter inrush from tripping the BMS.
Give this method a shot. If it doesn't work, use your charge controllers to quickly supply steady dc power to your inverter then turn on batteries. If this doesn't work, good luck.
 