There’s a recent good thread on this. And there are scores of threads on this in general. A couple below.
I feel like the two grounding rod deal may be misunderstood based on your diagram. I think the requirement is two grounding rods, not greater than 6 (?) feet apart, and bonded together. The purpose of which is to be a connection to the earth.
In my mind I think of these two rods as the single earth ground.
I don’t think this is what people think when they hear two grounding rods.
Not to criticize
@Supervstech at all but I have a hard time understanding “neutral must be separate from all grounding conductors except in the first disconnecting means….”
I think there is only one neutral ground bond and I guess the first disconnecting means is the breaker box?
PS-listen to
@Supervstech instead of me in all things.
I am about to do the trenching to bury all my cables, so need to get this straight I read @FilterGuy white paper on grounding for arrays (pt3) and am still confused. my setup is as follows 2 ground mount offgrid arrays 6kw each using ironridge racks,weebs, on top of 3" metal piping, 2 strings...