As shipped and unpowered, my TP6048 has its ac output N-G bonded. SGP help says there is a relay that unbonds when ac input is energized. So apparently this is a normally closed switch that will opens when the grid goes down and there is no other ac input. I have not been able to learn if there is a way to disable bonding. If not, I can only use this unit for circuits that are disconnected from neutral (or two-wire 220 circuits that don't have a neutral.)
SGP hasn't answered how this can be connected and the manual doesn't say. Elsewhere on this forum there is suggestion about rewiring the ground (on a different bonded inverter.) As all connected grounds are electrically one point, I don't see how that solves the parallel path issue unless the inverter is left ungrounded, surely wrong. Absent a solution I think I need a different inverter that can be set to never bond.
SGP hasn't answered how this can be connected and the manual doesn't say. Elsewhere on this forum there is suggestion about rewiring the ground (on a different bonded inverter.) As all connected grounds are electrically one point, I don't see how that solves the parallel path issue unless the inverter is left ungrounded, surely wrong. Absent a solution I think I need a different inverter that can be set to never bond.