EG4 batteries not charging to 100%

I had a similar issue of one battery only charging to 89% so I just did the firmware update (may 2024) and now it goes to 100% but the voltage doesn't. Note they are all in parallel in the cabinet. Fix one problem and the next pops up.
1715902738167.png
 
now it goes to 100% but the voltage doesn't.
My only guess is that one battery disconnected because of a high cell and now it has settled while it was disconnected and the others are still at absorb or float. After some time did that one reset and join the others? In parallel they should all be at the same voltage. Do you have access to individual cell voltages within each battery, or some way to test my hypothesis?
 
My only guess is that one battery disconnected because of a high cell and now it has settled while it was disconnected and the others are still at absorb or float. After some time did that one reset and join the others? In parallel they should all be at the same voltage. Do you have access to individual cell voltages within each battery, or some way to test my hypothesis?
I’m with Ampster, you can’t have batteries in parallel with any decent interconnect and have different voltages.
 
My only guess is that one battery disconnected because of a high cell and now it has settled while it was disconnected and the others are still at absorb or float. After some time did that one reset and join the others? In parallel they should all be at the same voltage. Do you have access to individual cell voltages within each battery, or some way to test my hypothesis?
I agree that something had to disconnect otherwise the voltage would have to be the same being in parallel with the other batteries.

I also just installed the EG4 LiFePOWER4 Communications Hub this weekend. I believe it reads the batteries every 3 minutes. I haven't played with that feature yet.

Right now I have the EG4 3kW on it. Getting ready to parallel 2 together. I have two more batteries to install in the cabinet too. Charging set for 56.2/54.0 right now.
1715920668316.png
 
I downloaded the Hub data on battery #4. The Communications Hub is doing what it is supposed to do. This is the only battery that isn't happy. Just passed 1 year old. Data attached.

Cell Voltage difference peeked at this point
MaxMinDelta
3.583.40.18

1715947593626.png
 

Attachments

  • Batt_4_CSV.zip
    26.4 KB · Views: 2
Last edited:
I had a similar issue of one battery only charging to 89% so I just did the firmware update (may 2024) and now it goes to 100% but the voltage doesn't. Note they are all in parallel in the cabinet. Fix one problem and the next pops up.
View attachment 215877

I would recommend isolating the battery at 54.5v and separately charging this until it reaches the correlating voltage of the other three. Once this is done, reintroducing the fourth battery to the pack to see if this is corrected.
 
I had an issue recently with soc drifting. One out of six batteries was showing only 78ah stored, with total capacity at 99.8ah. The low battery was at th3 same voltage as the high batteries. I disconnected all but the low battery, and ran some big loads on my system. Battery showed 0% soc at...51.5v I think. I kept the (30-60a) loads going until voltage dropped to 48v. As it recharged, the soc was more in line with it's brothers.

I want to point out that I charged the single battery up to 51v, then turned on the other (54v) batteries, one at a time, while monitoring the low battery with a clamp meter, and I never saw more than 30a going into the low battery. Doing this is usually recommended against, but I wanted to see what would happen. No bangs, no smoke,

Figuring the rest of the batteries might have drifted, I brought the whole bank down to 48v over the last few days, and am (slowly) recharging back to full. Despite the weather reports, the clouds moved in 😆

I want to point out, my house idles between 200-400w, which might be too low of a draw for the batteries to register, leading to this soc drift. They usually are charged to 100% every day (55.6v 1.5hr absorb for balancing, float at 54.0v), and almost never drain below 75%.
 
I would recommend isolating the battery at 54.5v and separately charging this until it reaches the correlating voltage of the other three. Once this is done, reintroducing the fourth battery to the pack to see if this is corrected.
I had an issue of running just #4 on a 1KW load. It cut out randomly. My goal was to run it down for a little bit and then charge it up. It would cut out but didn't give any inforamtion in the HUB. The other issue is that the Hub was powered off the buss with only that battery on so it turned off before it recorded anything. I captured it on Solar Assistant.
Batt_4_BMS_Open.png

I isolated problem child #4 and charging at 54.5V solo on the Chargeverter. Chargeverter.png

Monitoring via BMS, I see sell the BMS keep dampening Cell 2 & 9

Charging_4.png

Once I get everything charged up and balanced should I take it up to 56.2 for a bit to top it off. Will mentioned 57V.. Digital Info overload. Bulk/Abs 57.0 and Float 54.5 vs 56.2/54.5.

Longevity with optimal balance quality?! I need to get the system to be almost fully automated so it is Wife Proof during hurricanes while I am out helping others..
 
I have tried everything. I contacted support@signaturesolar.com for the first time so lets see how that goes.

Unable to get it balanced and over 55.31 Volts.
 

Attachments

  • Batt4 ini.txt
    1.8 KB · Views: 1
  • Battery 4 going into alarm.png
    Battery 4 going into alarm.png
    36.4 KB · Views: 4
  • Battery 4 issues.png
    Battery 4 issues.png
    135.1 KB · Views: 5
  • HUB_Batt_4a.jpg
    HUB_Batt_4a.jpg
    284.5 KB · Views: 4
  • HUB_Batt_4ac.jpg
    HUB_Batt_4ac.jpg
    256.8 KB · Views: 3
  • HUB_Batt_4b.jpg
    HUB_Batt_4b.jpg
    277.7 KB · Views: 4
Last edited:
It is just sitting there balancing away ⏳

Your pack is way out of balance - you're showing 109mv delta.
If this was mine, I would open it up and use a bench power supply to pull up those low cells (#1,3, & 15) the balancer may take a very long time to bring these into balance on it's own.
 
Your pack is way out of balance - you're showing 109mv delta.
If this was mine, I would open it up and use a bench power supply to pull up those low cells (#1,3, & 15) the balancer may take a very long time to bring these into balance on it's own.
Agreed.
If you don't have a bench supply you could also bleed off the high cells.
 
Could you set the BMS_Test tool to scan all batteries in your bank and post a screenshot of the "BatInfo" / "Multipacks" screen which will show cell voltages for each battery, all in a spreadsheet like screen.

On the "SinglePack" tab set the "Packs Number" to the number of batteries in the bank and set the "Start Adr" to the address of the first battery (most likely 1) then click the "Add address to sequence" button then select the "MultiPacks" tab. It will take a moment to populate as the BMS_Test scans each battery
 