I will have someone contact you for a RMA. I want to personally test your inverter when it comes in as well I can post the results here if you are ok with that. After you get a new replacement and this problems is still going on what would you suggest the problem is at that point?
I have know idea. I know I ran the same setup with 2 6548's and not once did the AC not start for 2 summers. When I first installed this inverter it shut down trying to start AC. Now after numerous firmware changes it will run AC.
 
I installed a new Micro Air today. The start amps are 32-33 amps now. But the light show I get everytime it starts is not good. So I'm not sure what is up but when I was on 1312 I use to get big blink on a hard start. Now I have 10-15 amp less hit and the lights flashing is terrible
Damn, that looks almost identical to mine. When you say "lights flashing" is that only during the start ramp or do they continue flashing following the start on the run cycle?
 
Damn, that looks almost identical to mine. When you say "lights flashing" is that only during the start ramp or do they continue flashing following the start on the run cycle?
Only flashes/blinks when AC is starting. Now that I have the AC start amps lower then they have ever been, I would have thought it would have been better. But I was on 1312 firmware before, and now I'm on 1616. Before, it was a blink/flash. Now, it is multiple blinks/flashes.
 
I did have 1919. That is what you removed and installed 1616. 1919 would start AC and then shut off after 5 sec. Then on 3rd try it said over voltage on the soft start.
 

Attachments

  • Screenshot_20240411_160130_EasyStart.jpg
    Screenshot_20240411_160130_EasyStart.jpg
    50.9 KB · Views: 7
Were you able to get this ironed out? Lots of 18kpv users on here that may benefit from a potential “fix” or might be happy to know if there was an “issue” found
 
So far yes. They have changed my firmware a few times. I also changed out soft start. This is my 3rd one. When I first had issues I went with a different brand that SS sells. It was no different so I went back to Micro Air so I can see the start amps. I just installed a new Micro Air. Not sure what was changed to change it. It runs AC no problem right now. But it's only 79 degrees here today. But seems like start amps are consistent and stay under 38 amps. Starts AC with 3000w load. When I get home I'm going to put 6000w on it and see how it does with AC
 
Were you able to get this ironed out? Lots of 18kpv users on here that may benefit from a potential “fix” or might be happy to know if there was an “issue” found
Here is what I just tested. Started AC with 6824 w already on. Went to 9884w with AC. Then I turned on a couple burners on oven and it went to 13.5kw. So all is good so far.

Inverter was great all winter. Just wasn't happy with my AC and now it seems happy all the time
 

Attachments

  • Screenshot_20240430_154003_Samsung Internet.jpg
    Screenshot_20240430_154003_Samsung Internet.jpg
    48.4 KB · Views: 10
  • Screenshot_20240430_154018_Samsung Internet.jpg
    Screenshot_20240430_154018_Samsung Internet.jpg
    50.9 KB · Views: 10
  • Screenshot_20240430_154122_Samsung Internet.jpg
    Screenshot_20240430_154122_Samsung Internet.jpg
    51.5 KB · Views: 10
Here is what I just tested. Started AC with 6824 w already on. Went to 9884w with AC. Then I turned on a couple burners on oven and it went to 13.5kw. So all is good so far.

Inverter was great all winter. Just wasn't happy with my AC and now it seems happy all the time
13.5kW is impressive for the 12k. How long will it handle that load without bypassing to grid? Are your loads well balanced between legs?
 
I don't have grid hooked up. It says 10 min at 14.7 kw and 5 min at 15.5 kw with solar. 13.5 kw with no solar.

I look at it as 12 kw. Playing the game of running more will end up shutting down your house. Nice to have a cushion. But I just would turn off any load over 12kw
 
Last edited:
Interesting on the micro-air. I would be curious to try without the micro-air at all. Thanks for the update.
Might try it tomorrow... I removed my micro-air to have it serviced last year. Ill try it on the 18k prior to installing back. the only difference is I'm running a 3 or 3.5 ton I forget.
 
@ksmithaz1 didn't work for me... forgot to update yall here 🙃.
Current setup: 18kpv with 20kw server rack and 4/0 cable. The 18kpv shut down and restarted on my three attempts. Also, I have 5kw+ of solar hooked up. I just had the 3.5 HVAC hooked up to give it a fighting chance. I need to try it again and take some readings. Also, I'm off-grid, so no grid assistance.
 
Last edited:
@ksmithaz1 didn't work for me... forgot to update yall here 🙃.
Current setup: 18kpv with 20kw server rack and 4/0 cable. The 18kpv shut down and restarted on my three attempts. Also, I have 5kw+ of solar hooked up. I just had the 3.5 HVAC hooked up to give it a fighting chance. I need to try it again and take some readings. Also, I'm off-grid, so no grid assistance.
What’s your station name? PM
Me and I can help you out.
 
Markus will get you sorted, these 18k inverters can handle 3-5ton AC systems easily.

Funny story. Today I was chasing a problem at my new home build with strobing lights when the inverter AC was running. We tried a couple of different firmware's on the 18K but nothing was making any difference at all. At Markus's suggestion I connected my Sol-Ark 12K to the house instead. Fortunately for the 18K and unfortunately for the AC system the problem continued (it needs a new inverter board even though it actually runs fine, weird). I'm working in the house laying flooring so I just turned the lights off and let the AC do it's thing. Then I needed to use the table saw to cut some vinyl plank and as soon as I hit the switch everything went off..... I didn't even think to consider how delicate the Solark 12K is when it comes to surge output.
So the 18K was promptly wired back up and I don't have to think about surge loads again.
 
So, we were having the same issue. I noticed the yellow arrows were feeding power to the EPS rather than standard consumption. I'm not sure what the EPS stands for but by reading what I did it was meant to be hooked up to a critical loads aka backup panel. Following the flow charts in the manual gets it set up this way.

What we did to fix it was turn OFF off grid mode. This moved the arrows to consumption mode rather than EPS. I don't know why EG4 labeled it the way it did, but EPS mode does not like very high inrush current. By switching this, we went from an 18kpv that wouldn't even start a 2 ton ac to one that would not only start the two ton, but start a 4 ton on an easy start with the 2 ton running and about 2k worth of normal loads.

I'm not sure how it'll work without grid connection but I would think it would do the same.

In brief, if your 18kpv won't start ac even with micro air soft start, turn OFF off grid mode.
 