I am wiring up an MPP PIP 2024 LV-MK All-in-One unit in my Surveyor Legend Travel trailer. I am planning on diverting the AC power in from shore power directly into the all-in-one and then connecting the output of the all-in-one into where the shore power came into the main AC breaker box of the trailer. With the net result that if I am plugged into shore power, the AIO goes into bypass mode and everything in the trailer is powered from shore power, and if I am not plugged in then everything will run off the inverter. (and I will use a 24v to 12v buck converter to power the 12v system)
First question:
Does that seem reasonable? I know I can only put out 2000w (16amps at 120v) while on inverter mode but I also know the trailer technically has a 30 amp plug. Would I be ok to run anything I wanted in the trailer while in bypass mode? Like the Air Conditioner at the same time as the microwave? or is pushing that much through the AIO not ok, even when it is in bypass mode?
Second question:
I have some leftover Romex simpull awg 10 CU 3 CDR with AWG 10 Ground wire. can I use that wire for both the A/C in AND A/C out of the all-in-one? as in, can I wire the black wire to the LINE of the input, the red wire to the LINE of the output, the white wire to Neutral of BOTH the input AND output, and the Ground to both the Ground of the input and the Ground of the output? I feel sheepish even asking that question and I for sure can just get some 10/2 wire and wire it like normal but I figured I'd at least ask so I could learn why that would not be ok.
First question:
Does that seem reasonable? I know I can only put out 2000w (16amps at 120v) while on inverter mode but I also know the trailer technically has a 30 amp plug. Would I be ok to run anything I wanted in the trailer while in bypass mode? Like the Air Conditioner at the same time as the microwave? or is pushing that much through the AIO not ok, even when it is in bypass mode?
Second question:
I have some leftover Romex simpull awg 10 CU 3 CDR with AWG 10 Ground wire. can I use that wire for both the A/C in AND A/C out of the all-in-one? as in, can I wire the black wire to the LINE of the input, the red wire to the LINE of the output, the white wire to Neutral of BOTH the input AND output, and the Ground to both the Ground of the input and the Ground of the output? I feel sheepish even asking that question and I for sure can just get some 10/2 wire and wire it like normal but I figured I'd at least ask so I could learn why that would not be ok.