Alpine_Junky
New Member
In the process of adding a 2nd midnight 200 charge controller to a pre-wired Schneider sw4048 currently running a single midnight 200 purchased from a reputable on-line seller.
My question - when they sent me the 2nd charge controller, I also asked for 2 more breakers. Instead of sending me 2 single poles, they sent me 2 double poles (single switch, double pole midnight midmnedc-80-300 breakers). The midnight box only has room for 4 breakers total - and the current charge controller is taking up 2 of these slots. The problem - I can't fit the breakers they sent plus the existing ones & would have thought that each charge controller should have its own separate breaker set.
I am questioning - 1) Did they send me the wrong breakers? Should I have simply received a duplicate set of single poles? (Plenty of room, no questions) 2) Did they send me the right breakers and am I overlooking that I should be wiring both charge controllers on the same set of breakers?
I don't think this matters but I have 2 arrays: one with 6 panels (2280 watts, 2 strings of 3 making 120V in and around 21amps short circuit), the other with 9 panels (3420 watts, 3 strings of 3 making 120V in and around 31.5 amps short circuit). All 15 panels matched 380w silfab. Combined, these would not exceed the 80 amp breakers sent.
My question - when they sent me the 2nd charge controller, I also asked for 2 more breakers. Instead of sending me 2 single poles, they sent me 2 double poles (single switch, double pole midnight midmnedc-80-300 breakers). The midnight box only has room for 4 breakers total - and the current charge controller is taking up 2 of these slots. The problem - I can't fit the breakers they sent plus the existing ones & would have thought that each charge controller should have its own separate breaker set.
I am questioning - 1) Did they send me the wrong breakers? Should I have simply received a duplicate set of single poles? (Plenty of room, no questions) 2) Did they send me the right breakers and am I overlooking that I should be wiring both charge controllers on the same set of breakers?
I don't think this matters but I have 2 arrays: one with 6 panels (2280 watts, 2 strings of 3 making 120V in and around 21amps short circuit), the other with 9 panels (3420 watts, 3 strings of 3 making 120V in and around 31.5 amps short circuit). All 15 panels matched 380w silfab. Combined, these would not exceed the 80 amp breakers sent.