Solar Joules are catch and release
OK, it's Isc but you are getting reasonable numbers.Thanks, I just put three panels in series that are getting Sun at this time of the day 6:50 pm EST.
VOC 115.4V
AoC 9.7 A
OK, it's Isc but you are getting reasonable numbers.Thanks, I just put three panels in series that are getting Sun at this time of the day 6:50 pm EST.
VOC 115.4V
AoC 9.7 A
That inverter has TWO MPPT inputs. Each could connect to one string of between 3 and 9 panels.I only have all in one inverter.
With 2 MPPTS.I only have all in one inverter.
Agreed.I'd probably put all eight panels into one string, then you won't have any question about meeting the MPPT minimum input voltage, and you'll generate more power during the day, and have less line loss.
Is the inverter reading voltage on that array? Does it say anything about what mode it's in or why it's not making power or charging your batteries?But the Inverter is not recognizing any amps on the display.
Ok, that will be my next test tomorrow morning. Thank you for your response.It looks like it needs 150V from the panels to run, use at least 4 maybe all 8 as that is well under the limit it can handle.
Also check the error logs.
I will check the Voltage reading on the Inverter display tomorrow when it is Sunny. The Inverter has been on Battery mode all along which is why the battery SOC reduced to close to 5%. It did alarm when SOC went below 15% and 10%.Is the inverter reading voltage on that array? Does it say anything about what mode it's in or why it's not making power or charging your batteries?
Thank you for correcting it.OK, it's Isc but you are getting reasonable numbers.
Got it. Excellent suggestion. I will try it on the other MPPT as well. Thank you!That inverter has TWO MPPT inputs. Each could connect to one string of between 3 and 9 panels.
Thank you for your response./*
<Not sure why this came out so huge, can't seem to edit it, sigh>
Maximum input power 11,000 W Maximum Input Current 22/22 A Maximum open circuit voltage 500 Vdc MPPT operating voltage range 125 Vdc−425 Vdc
*/
I charged the batteries via Utility/Grid yesterday night to SOC 90% by changing the parameter 6 temporarily (to Utility can charge batteries if Solar power is not available) and it charged fine.So worst case is a defect in the charge controller portion, right? Panels could deliver current, but the controller does not pull current because it falsely "thinks" the batteries are full or there are no batteries.
I would focus on the connections AIO to battery bank. Maybe swap batteries, remove some batteries from the bank, reset the BMS if that's possible. Somehow the charger doesn't want to charge them.
Have you tried charging them from AC with the AIO?
If you don’t have grid-in, have you tried charging the batteries with a portable 54V charger?
I have put 7 panels in series last night and the voltage at the inverter is 320V. The Inverter display is reading around the same amount. The amps are still 0 on the inverter.That inverter has TWO MPPT inputs. Each could connect to one string of between 3 and 9 panels.
Your battery is showing as full
True.I initially thought the same, but SOC was 5% at the beginning of this thread.