So I am running a SRNE 100/40A Charge Controller on a 24v battery bank. A shop recommended me two trina solar 500 watt vertex panels with these specs:
500 Watt Panel
Open Circuit Voltage (V) 51.70
Maximum Power Voltage (V) 42.80
Maximum Power Current (A) 11.69
Short Circuit Current (A) 12.28
They told me to wire in series but It looks like I'll over exceeed the VOC since it will be 103+. I am thinking of just wiring in parallel myself so the VOC will still be 51.70 way under the 100v limit. I know that these numbers vary with temperature right? Just trying to figure out what to do before I blow some stuff up lol. Simple question, let me know. I don't know who else to ask since this is the only solar shop really where I am physically located.
So I am running a SRNE 100/40A Charge Controller on a 24v battery bank. A shop recommended me two trina solar 500 watt vertex panels with these specs:
500 Watt Panel
Open Circuit Voltage (V) 51.70
Maximum Power Voltage (V) 42.80
Maximum Power Current (A) 11.69
Short Circuit Current (A) 12.28
They told me to wire in series but It looks like I'll over exceeed the VOC since it will be 103+. I am thinking of just wiring in parallel myself so the VOC will still be 51.70 way under the 100v limit. I know that these numbers vary with temperature right? Just trying to figure out what to do before I blow some stuff up lol. Simple question, let me know. I don't know who else to ask since this is the only solar shop really where I am physically located.