Alarm always on? short circuit. Manual says disconnect the power cables, and check
Gave a little more thought to this post as I drove back down to the valley. The Alarm light isn't always on. I can turn on the BMS and the battery's breaker and there is no alarm. When I do that, I test 52 volts on the inverter's battery lugs which shows that the battery is sending power up to them. There is no continuity between positive and negative, nor is there continuity with anything else. There are no shorts, faults or alarms on the battery until I turn on the inverter's battery breaker. The instant I switch on the inverter's breaker, I hear a "click" from each battery and the red alarm lights come on.