When sizing wire between batteries, fuses, inverter, bus bar, breaker box/fuses, etc.
My set up:
Panels: 1100W panels (6 x 185W)
CC: 60A
Battery system: 24V, 4800Wh, 12V x 4 @ 100Ah each, LiFePo4, 2s2p
Inverter: 3000W 24V
When is the wire too big?
When does upsizing become pointless?
Efficiency increase? Ie. once you size up to a specific size, you will have as much efficiency as possible, and sizing up would NOT increase it. Where is that point?
Ex.
Panels: 10AWG, but does 8AWG make a difference? Chart says 10AWG at 60° can handle up to 30 amps, 4AWG 60° insulation can handle 70A, and since my CC can do 60A, isn't it prudent to use 4AWG? I realize there are other factors that change PV wire size (CC panel wire receptacle size, how panels are wired (series vs parallel), but is my logic and understanding sound?
Ex.
Batteries: Wire between batteries: 6AWG, but size up 4AWG? Unnecessary? Worth it? Obviously, bigger isn't gonna hurt, but will 4/0 provide greater efficiency vs 6AWG? What's minimum wire size for max gain?
Ex.
Inverter wires, what size? Since the current is higher and due to inverter efficiency losses (80% efficiency let's say for worst case scenario), I'd assume that sizing up here would be critical to reduce V drop, efficiency, proper heat dissipation, etc. but size up and stop at what size?
I want a safe, high quality, long lasting system. Calculate the minimum wire size for the load, but then how much bigger is good to give a safety buffer and maximal efficiency?
How is wire size between batteries determined?
Thanks in advance.
My set up:
Panels: 1100W panels (6 x 185W)
CC: 60A
Battery system: 24V, 4800Wh, 12V x 4 @ 100Ah each, LiFePo4, 2s2p
Inverter: 3000W 24V
When is the wire too big?
When does upsizing become pointless?
Efficiency increase? Ie. once you size up to a specific size, you will have as much efficiency as possible, and sizing up would NOT increase it. Where is that point?
Ex.
Panels: 10AWG, but does 8AWG make a difference? Chart says 10AWG at 60° can handle up to 30 amps, 4AWG 60° insulation can handle 70A, and since my CC can do 60A, isn't it prudent to use 4AWG? I realize there are other factors that change PV wire size (CC panel wire receptacle size, how panels are wired (series vs parallel), but is my logic and understanding sound?
Ex.
Batteries: Wire between batteries: 6AWG, but size up 4AWG? Unnecessary? Worth it? Obviously, bigger isn't gonna hurt, but will 4/0 provide greater efficiency vs 6AWG? What's minimum wire size for max gain?
Ex.
Inverter wires, what size? Since the current is higher and due to inverter efficiency losses (80% efficiency let's say for worst case scenario), I'd assume that sizing up here would be critical to reduce V drop, efficiency, proper heat dissipation, etc. but size up and stop at what size?
I want a safe, high quality, long lasting system. Calculate the minimum wire size for the load, but then how much bigger is good to give a safety buffer and maximal efficiency?
How is wire size between batteries determined?
Thanks in advance.