The Expert Power 3000 watt inverter came Monday in the rain.
Got it hooked up today to test out. It arrived double boxed with closed cell foam packing in the inner box. It comes with a remote on/off/ Power save switch, mounting brackets, a 30 ohm 25 watt pre charge resistor, 2 cables about 6 feet long and manual. The cables are about 1/0 and the ring lugs are crimped and
@Will Prowse, soldered. Manual calls for 3/0.
Initial test data 0.28 amp spike through pre charge resistor. Power save mode 0.3 amp and on mode 7.8 amps . Batteries started at 13.33 volts. Floor fan on low 9.96 amps/31watts. All values reported by Victron 500 amp smartshunt.
For higher wattage values I used a heat gun and small electric heater. 1840 watts for the heat gun, 815 watts on low for the heater and 1293 watts on high. Again wattage reported by the smart shunt. By varying settings of the heat gun and space heater I ran the inverter at 3420 watts, 270.4 amps for 5 minutes. Positive inverter cable was hot enough to burn you. Put the heat gun and space heater on fan only and let the unit cool down. 1.7kWh used during the test.
Next made up a suicide cord and tested the buit in charger. Charge ran between 58.6 and 59.3 amps. There was some kind of noise on the DC out. No scope so don't know what it looked like. 1.4kWh brought the batteries back to 99%.
Battery charging was a little uneven but that was due to mismatched cables.
Over all not a bad inverter for $619. One thing I don't like is no way to turn it on without the remote switch and no cover over the ac input/output terminals.
It will work fine with 400 aH Battery bank for a few hours to run a 15000 BTU roof air on the RV.