200 amp vs. 100 amp Inverter pass through
For 30+ years customers have requested whole house backup. This goes all the way back to my Trace Engineering days in the early 1990’s. We barely had a 60 amp bypass relay in our inverters back then. I suppose we could have used an expensive external 200 amp contactor, but we couldn’t justify trying to run the entire house from a 4000 watt inverter, so we talked the customers out of that idea. OK, jump decades into the future and has the story changed? Yes and no. Some very popular All In One inverters now have internal 200 amp relays and breakers. So, can you just put these inverters between your utility meter and the main distribution panel? Physically you sometimes can, but it isn’t quite that simple. This type of connection is not legal in North America.
Not Legal??? It is being done every day! Well probably not as simple as stated above. You see those 200 amp circuit breakers built into the inverter have only a 5000 amp interrupt rating. They are not designed for or approved for direct connection to the utility. They are not rated as a service disconnect. So how you ask are they doing it?
There must be a utility approved disconnect/overcurrent device upstream from the 200 amp inverter!
These devices aren’t cheap and neither is the labor to connect them. It will require a licensed electrician to schedule and connect equipment directly to the utility. Approvals for this type of connection are somewhat more complicated than merely adding circuits to an already existing distribution panel. A 200 amp bypass switch may be required in your jurisdiction and they are expensive, but it is a very good idea anyways. You will also be required to change your grounding as it is no longer to come from the main distribution panel. The grounds now have to be moved to the service disconnect. None the less some customers believe it is much simpler to have the whole house run off the inverter during an outage. The simple answer is it can be done just fine. If you have an inverter capable of powering a fair amount of your larger loads and a battery bank capable of supporting them for the intended time, it can be a great way to go. Plan on multiple inverters and literally tons of batteries. Unfortunately, in most cases a single inverter isn’t going to do the job. Today’s inverters are now rated for as much as 10,000 to 12,000 watts of continuous output. Here is a simple math exercise for you to ponder. Electric range (12,000 watts), Hot water heater (5,500 watts), Electric clothes dryer (5,000 watts), Air conditioners (3500 watts each), fridge (800 watts), EV charger (7,200 watts). Lights, up to 1000 watts, hot tub (don’t even go there). Now you wouldn’t normally have most of these on at the same time, but even just a couple along with lights and TV can and usually will put you over your inverters power capability. When that happens the inverter will shut off to protect itself. These loads listed amount to 35,000 watts. It is quite conceivable that one or more of these large loads could be on during an outage. We haven’t really even included normal loads such as toasters, microwaves, lights, TV, and such. If you are like my wife, there might be a wine cooler, freezer, espresso machine hair curler etc. You just can’t tell when there will be a utility outage and you certainly aren’t going to plan your electrical usage based on what ifs! No worries, the industry has a solution for this. Look at the picture to the right.
This is a concept of what a Load shed box or system might look like.
Here is how the story might go after your first utility outage. The day after your utility outage occurs and your nice new shiny inverter system just shut off rather that supplying your whole house, you call your installer. You and your family are confused why the new expensive back up system failed to back anything up. Just so you know, installers hate getting these calls. And you hate going around in the dark trying to figure out how to get the power back on. Nothing is obvious. You were probably warned this could happen during the quoting phase, but you declined the additional $4,000 to $8,000 to add a load shedding box/system. Afterall, the utility disconnect/bypass already cost you thousands more and wasn’t anticipated. There are a couple of ways this would work though. Some load shedding boxes are nothing more than relays that will shut off circuits once there is a utility outage. Those boxes have between 3 and 8 relays. Wiring is run from the main distribution panel to the relay box and then back again. This system would immediately shut off your large loads. Kind of messy. Another method would be more elegant and programmable. (more expensive, but still just as messy) This would look at battery voltage or state of charge and will shut off certain circuits based on how they were programmed to act. This now requires communications between the battery bank, inverter and relays. It is also possible to use shunt trip circuit breakers with an associated power supply and control system, but they will not turn themselves back on once the utility comes back on. Plus, they will not fit inside the main distribution panel.
So you can see these 200 amp inverters can back up your whole house as long as you don’t mind spending thousands more for multiple inverters and very large battery banks. You can likewise design a system to shut off part of your house during an outage. Hmmmm, something just doesn’t sit right with either scenario? You pay for a whole house back up system, but have to shut off certain parts of it due to inadequacies of the products plus you have additional expenses and complexity. There is a big difference between running a few loads during an outage and attempting to run a utility connected home off-grid during an outage. All off-grid homes run “whole house” 24/7. This is something we know about. In 35 years of designing manufacturing these inverters and systems, we have heard every horror story imaginable.
How do you avoid these problems? Glad you asked. We at MidNite Solar have been involved in most of the truly great off-grid inverter companies for over 30 years and we actually know how to deal with limited inverter and battery capacity. Now if money is no object or if you think your inverter would never shut down during an outage, you can stop reading.
- We do not want an expensive 200 amp disconnect/overcurrent and AC bypass switch device to be required in front of the inverter on the utility side.
- We need to deal with these large house loads without requiring an external load shedding box that costs thousands of dollars.
The first thing we did is what we have always done. Design for a 100 amp sub panel for all critical loads. We know from history that utility outages are mainly about
lights, TV and cold beer! That may be a bit over simplified, but you get the idea. Select the circuits that you absolutely can’t live without during an outage. We provide four 120V circuit breakers to aid in this, but a separate 125 amp sub panel may make more sense. You can also use the four 15 and 20 amp breakers built into our inverter for backing up circuits of choice. Lights, AC outlets, fridge, microwave, TV or two, water and sewer pumps, freezers, etc.
Then since you don’t know how long the outage will last, we added three 120/240VAC programmable load circuits. If the outage is brief, why shut down some of your larger important circuits? We added one 30 amp, one 50 amp and one 60 amp circuit complete with breakers and programmable relays. This is actually six 120VAC or three 120/240VAC circuits or a combination of both depending on how they get configured on-site. It is up to you and your installer to decide what circuits to back up, so choose wisely. The goal is that these included programmable load shedding circuits will suffice for all but the most demanding home. These three programmable load shedding circuits will also save the customer many thousands of dollars over an external load shed solution. The good thing is these breakers and relays are already included in the MidNite inverter. You can program them to turn on and off based on battery voltage, battery state of charge, utility outage length of time etc. They operate totally automatic. No intervention is required once set up.
One of the things that can also force an inverter to unexpectedly shut off is the surge that some loads demand when turning on.