Hmmm.. There are 4 things on that bus Bar. The Battery, the SCC, the Inverter and the Fuse block.Would I need to have a positive and neg busbar or could I use the neg on the fuse block?
The inverter and the charger are rated at higher amperage than the Fuse-block can handle so those can't go through the fuse block. The *proper* way to deal with it is a bus bar. Having said that.... You have 3 'large' connection points: 1)The battery, 2) the inverter and 3)The large common negative on the fuse blocks. If you can hook all 4 items together without more than two lugs per connection, you might be a be able to make it work.
(I recommend the bus bar).
The box is rated 30 amp per connection and the individual circuits are protected by breakers at the switch box. So, yes 30 amp fuse is what I would use, but make sure the wire to the switch box can handle 30 amps.Also would fuse #2 be a 30 amp? Or how do I calculate that? Would that be a calculation of the appliances all together?