Hi,
i have 8x109ah 12v alphacell 220 gxl batteries that came out of cell towers.
they will be parallel as they are replacing 12v flooded batteries.
i am having some confusion about charge controller settings.
the only specs written on the batteries is the float voltage(13.5-13.8)
spec sheet
doing some searching i found a users manual
according to that page..
bulk/float: 2.27v/cell = 13.62
accept: 2.4v/cell = 14.4v
reading on the forums voltage should never be over 14.1 for gel batteries?
so i'm confused about this.
from the tracer manual default settings for gel
Over Voltage Disconnect: 16.0V
Charging Limit Voltage: 15.0V
Over Voltage Reconnect Voltage: 15.0V
Equalize Charging Voltage: ——
Boost Charging Voltage: 14.2V
Float Charging Voltage: 13.8V
Boost Reconnect Charging Voltage: 13.2V
Low Voltage Reconnect Voltage: 12.6V
Under Voltage Warning Reconnect Voltage: 12.2V
Under Voltage Warning Voltage: 12.0V
Low Voltage Disconnect Voltage: 11.1V
Discharging Limit Voltage: 10.6V
Equalize Duration: ——
Boost Duration: 120 min
based on what i have read(and the specs above) shouldnt i be using something like this..
Over Voltage Disconnect: 14.2V
Charging Limit Voltage: 13.6V
Over Voltage Reconnect Voltage: 13.5V
Equalize Charging Voltage: ——
Boost Charging Voltage: 14.1V
Float Charging Voltage: 13.6V
Boost Reconnect Charging Voltage: 13.2V
Low Voltage Reconnect Voltage: 12.6V
Under Voltage Warning Reconnect Voltage: 12.2V
Under Voltage Warning Voltage: 12.0V
Low Voltage Disconnect Voltage: 11.8V
Discharging Limit Voltage: 11.5V
Equalize Duration: ——
Boost Duration: 120 min
another question i have is i have a iota dsl-90 charger
the iq4 smart controller i had for the flooded batteries is not useable for gels(voltage too high)
would be ok if i use it without the smart controller and use the dual voltage jack plug.
the charger is only used when generator is running.
i can monitor the batteries via my shunt.
i was thinking of charging to 13.6 then 14.2(or vice versa) using the plug when needed.
maybe just charge to 13.6 using it and let the solar handle the boost?
thanks
mike
i have 8x109ah 12v alphacell 220 gxl batteries that came out of cell towers.
they will be parallel as they are replacing 12v flooded batteries.
i am having some confusion about charge controller settings.
the only specs written on the batteries is the float voltage(13.5-13.8)
spec sheet
doing some searching i found a users manual
Battery System Float Charging - Alpha alphacell gelcell series User Manual [Page 20]
Alpha alphacell gelcell series Manual Online: Battery System Float Charging. Battery System Float Charging Voltage NOTE: The following set points are recommended for AlphaCell Batteries when used with the xM Series 2 or GMx Power Supply. 20 Encountering temperature extremes When you...
www.manualslib.com
according to that page..
bulk/float: 2.27v/cell = 13.62
accept: 2.4v/cell = 14.4v
reading on the forums voltage should never be over 14.1 for gel batteries?
so i'm confused about this.
from the tracer manual default settings for gel
Over Voltage Disconnect: 16.0V
Charging Limit Voltage: 15.0V
Over Voltage Reconnect Voltage: 15.0V
Equalize Charging Voltage: ——
Boost Charging Voltage: 14.2V
Float Charging Voltage: 13.8V
Boost Reconnect Charging Voltage: 13.2V
Low Voltage Reconnect Voltage: 12.6V
Under Voltage Warning Reconnect Voltage: 12.2V
Under Voltage Warning Voltage: 12.0V
Low Voltage Disconnect Voltage: 11.1V
Discharging Limit Voltage: 10.6V
Equalize Duration: ——
Boost Duration: 120 min
based on what i have read(and the specs above) shouldnt i be using something like this..
Over Voltage Disconnect: 14.2V
Charging Limit Voltage: 13.6V
Over Voltage Reconnect Voltage: 13.5V
Equalize Charging Voltage: ——
Boost Charging Voltage: 14.1V
Float Charging Voltage: 13.6V
Boost Reconnect Charging Voltage: 13.2V
Low Voltage Reconnect Voltage: 12.6V
Under Voltage Warning Reconnect Voltage: 12.2V
Under Voltage Warning Voltage: 12.0V
Low Voltage Disconnect Voltage: 11.8V
Discharging Limit Voltage: 11.5V
Equalize Duration: ——
Boost Duration: 120 min
another question i have is i have a iota dsl-90 charger
the iq4 smart controller i had for the flooded batteries is not useable for gels(voltage too high)
would be ok if i use it without the smart controller and use the dual voltage jack plug.
the charger is only used when generator is running.
i can monitor the batteries via my shunt.
i was thinking of charging to 13.6 then 14.2(or vice versa) using the plug when needed.
maybe just charge to 13.6 using it and let the solar handle the boost?
thanks
mike