Victron Ground Neutral bonding with parallel units

JeffG

New Member
Joined
Apr 21, 2021
Messages
24
Hey all,

My understanding is Victron has a dynamic GN bonding relay in their MP2's. By dynamic, I mean when connected to shore power the relay is open and the bonding takes place in the shore power panel and when inverting the MP2 closes the relay which bonds the GN inside of the MP2.

If the above is true, wouldn't you have a double bond while inverting if you had 2 MP2's connected in parallel?

Jeff
 
Hey all,

My understanding is Victron has a dynamic GN bonding relay in their MP2's. By dynamic, I mean when connected to shore power the relay is open and the bonding takes place in the shore power panel and when inverting the MP2 closes the relay which bonds the GN inside of the MP2.

If the above is true, wouldn't you have a double bond while inverting if you had 2 MP2's connected in parallel?

Jeff

Yes. That's why you disable the N-G bond in all but the first unit, i.e., only unit #1 toggles the bond as you describe. The others never engage the bond.
 