Mine says "no limitation"....and I didn't change it to that so I'm assuming that's default?
the max ac input is the max power that the inverter will pull from the grid without tripping the grid input breaker. For example if the grid input breaker is 125A*80%=100A*240=24kw.
if you use 200A leave it as default no limitation or 6553.5.
 
the max ac input is the max power that the inverter will pull from the grid without tripping the grid input breaker. For example if the grid input breaker is 125A*80%=100A*240=24kw.
if you use 200A leave it as default no limitation or 6553.5.
So what would it be set to for a grid input breaker of 40 Amps. 6553.5/200A = 32.7675 X 40 = 1310.7? thanks
 