HEllo,
I have two Axpert 5.6kw inverters setup in parallel, running for months now without issue. I added a third today, configured cables and menuitem 28 to PAL as per manual, and it goes straight to battery voltage fault error 83.
From left to right:
Inverter 1: Firmware 05606 (New inverter)
Inverter 2: Firmware 05605 (Master)
Inverter 3: Firmware 05600 (Slave)
The above pic was taken when I reverted back to the working dual parallel.
I have tried the following:
Swapped battery cables from 2 to 1 and from 1 to 2. Inverter 1 still throws error 83, shuts down and causes CAN error 80 on Master.
Configured inverter 1 and 2 in parallel without inverter 3. Inverter 1 still throws error 83, shuts down and causes CAN error 80 on Inverter 2.
Started Inverter 1 first as master, inverter 2 and 3 both throws error 83, both shutdown and cause CAN error 80 on Inverter 1.
All roads lead to the new inverter it seems, noting that it runs fine on its own.
I have two Axpert 5.6kw inverters setup in parallel, running for months now without issue. I added a third today, configured cables and menuitem 28 to PAL as per manual, and it goes straight to battery voltage fault error 83.
From left to right:
Inverter 1: Firmware 05606 (New inverter)
Inverter 2: Firmware 05605 (Master)
Inverter 3: Firmware 05600 (Slave)
The above pic was taken when I reverted back to the working dual parallel.
I have tried the following:
Swapped battery cables from 2 to 1 and from 1 to 2. Inverter 1 still throws error 83, shuts down and causes CAN error 80 on Master.
Configured inverter 1 and 2 in parallel without inverter 3. Inverter 1 still throws error 83, shuts down and causes CAN error 80 on Inverter 2.
Started Inverter 1 first as master, inverter 2 and 3 both throws error 83, both shutdown and cause CAN error 80 on Inverter 1.
All roads lead to the new inverter it seems, noting that it runs fine on its own.