zanydroid
Solar Wizard
Where I am this stuff is checked at plan submission time, but after that they just trust that you followed the plan.
As I read the code, it isn't just the Polaris that counts as a busbar, it is all the "tap" wires as well; it precludes the use of the tap rule. Your inspector might have a more generous interpretation though.I think Polaris, which acts as a busbar, is good for something like 400A. I'll put grid and PV backfeed at opposite ends of it, anyway.
It will be fed from 200A main breaker, and taps will go to various breakers and fuses each protecting at 100A, 125A, or 200A, no daisy chain to additional OCP. The wires will have ampacity for at least either 125A or 200A.
Another DIY trick I’ve heard is to use your hybrid inverter to backup your loads while you amateurishly mess around slowly (no shame, you’re not a pro). This would also work for an in place replacement, theoretically. Have PG&E turn off power, take the next week to mess up a few times and have to call inspector back twice to get the all clear to turn back on. Might be two to three weeks if the inspection schedule is backed up ?
You can use that $3500 savings from paying someone towards a nice inverter or battery
Yes, the Zinsco was replaced by the Siemans. At the time It was difficult finding a 200 Amp surface mount solare ready panel and I paid full retail at one of the most expensive supply houses in my area who was the only one who had one in stock so it cost about $650 if I remember correctly.was the Zinsco panel completely replaced by the Siemens ? how much was the cost for that ?
The hype was not from anyone trying to make a buck. I have heard it mentioned on several boards. Since I have two EVs that I sometimes charge simultaneously I thought it was a wise risk management move. I did mention it to the PGE planner in the hopes it would expedite the upgrade. I was pleased with how fast they scheduled a crew to run the new drop.and also questioning the Zinsco danger hypes.
As I read the code, it isn't just the Polaris that counts as a busbar, it is all the "tap" wires as well; it precludes the use of the tap rule. Your inspector might have a more generous interpretation though.
I hear you, we're a 3-EV household. I've derated all chargers to max out ~15A each. All the push for "fast" charging is so unneccessary for home charging, when there's so many hours overnight. But yeah, the old Zinsco stuff is a concern. Is it true that the newer Zinsco breakers from Connecticut Electric are safe and approved ?The hype was not from anyone trying to make a buck. I have heard it mentioned on several boards. Since I have two EVs that I sometimes charge simultaneously I thought it was a wise risk management move.
That is why they cost so much. I bought a couple in the interim. I should sell them on eBay.Is it true that the newer Zinsco breakers from Connecticut Electric are safe and approved
then why not just replace all breakers with these ? assuming the AL bus bars are goodThat is why they cost so much. I bought a couple in the interim. I should sell them on eBay.
If you think thermal magnetic breakers are expensive imagine the fancier breakers (GFCI AFCI etc)then why not just replace all breakers with these ? assuming the AL bus bars are good
I did not have that knowledge at the time. I also thought I needed a bigger panel. I was already committed two new subpanels inside that garage wall and I could easily have fed them with new breakers that are apparently much safer. I have subsequently learned that an intellegent panel like a Span and others can manage loads in such a way that my 8kW solar system would most likely not need a solar ready panel with a 225 Amp busbar.then why not just replace all breakers with these ? assuming the AL bus bars are good
I get your logic; the difference is the bus finger is protected as a UL assembly; you can't get a 200A breaker that connects to a single bus finger (at least outside of an I-Line panel). Please post back if you get any issues from your inspector though.I consider each tap wire from Polaris same as a finger on busbar. They are protected by a single breaker.
just fyi, we have been running a HPWH (GeoSpring) since 2013 and always using HP without the resistive heat-rod. In fact, I've disconnected power to the upper/lower rods completely couple years ago in order to make sure my battery setup can handle the load during outage. The compressor has spec'd LRA=19.6A and RLA=4.5A (at 240vac). The clamp meter measured ~3.5A run time and the 5kw MPP AIO has no problem starting it. It's installed in my basement, welcomed side benefits include keeping the basement drier and abundant collection of clean condensate (distilled water ?)Successful 200A OH service upgrade and Hybrid inverter connection
I just passed my DIY 200A OH service upgrade in PGE territory. Previously I had just a meter socket and a 100A connection to my main panel which was very crowded and would prevent me from installing new appliances like induction cooktop and HPWH. I installed a new meter + panel and moved my...diysolarforum.com
there were much to learn in the early days and a lot of unknowns. My first rooftop went on in 2007 and code has evolved quite a bit.I did not have that knowledge at the time. I also thought I needed a bigger panel. I was already committed two new subpanels inside that garage wall and I could easily have fed them with new breakers that are apparently much safer.
Span has an interesting concept, but potentially unreliable with all those "features". How does it control each circuit breaker ? relays ?I have subsequently learned that an intellegent panel like a Span and others can manage loads in such a way that my 8kW solar system would most likely not need a solar ready panel with a 225 Amp busbar.
I get your logic; the difference is the bus finger is protected as a UL assembly; you can't get a 200A breaker that connects to a single bus finger (at least outside of an I-Line panel). Please post back if you get any issues from your inspector though.
what is a "Hawaiian Tie-In" and CSED ?Also available in Homeline. I might in the future try to do "Hawaiian Tie-In" for my sister's house, which has a center-fed CSED. This 200A branch breaker has four handles ganged, should work with interlock if desired (interlock depending on main breaker type and location.)
what is a "Hawaiian Tie-In" and CSED ?
the Polaris is a good option for my so-crowded Zinsco, to tap the N-bar to feed sub-panel(s).
Just discovered decent source with decent pricing (but w/ shipping, so bundle up): https://www.gordonelectricsupply.com/
are there other sources out there ?