I can see that circuit in the diagram. You made me look. The guy on the phone at champion said to unbond it to just remove the wire at the frame… but the diagram says differently as apparently you are aware.
Since ‘the shop’ will be supplied from a breaker panel (currently) fed from the ‘house’ 2kW inverter and the 1012LV-MK is NOT supplying the house- charging by solar and/or generator only- and the 1012 disconnects its N-G bond when the grid/gen-to-house homerun is energized …
So basically I need to think about that a bit more and come up with a no-mix wiring scheme. I already have six 10ga thhn in conduit (not yet in service) so I can keep the 1012 incoming circuit and the 2kW output circuits holy.
But thanks for pointing out the 6250 bond inside the rig- I “knew” that was on the diagram but hadn’t thought about it yet.
Edit
Probably just going to wire the shop breaker panel from the generator looking ahead to a 6048 or a couple 6548s, and just power a couple independent outlets and a light from the ‘house’ feed. Saves a couple things from needing attention.